[wxsig] How to make T238+ re-run sensor setup

sbm at ottix.net sbm at ottix.net
Fri Jul 5 07:21:57 CDT 2013


Thanks Will,

 	I have checked and it seems the bus is indeed looking good.  When 
I first plugged in the sensors, everything came up fine including being 
asked about performing sensor setup.  After reloacting (involving shutting 
down the power), and powering back up, the T238 would hang about 1.5 
heartbeats (according to the blinking LED) into the display showing "One 
moment please...".  I backed out, reseting (but not powering down) each 
time I removed a suspected sensor and isolated it to one.  Strange how one 
which behaved fine now doesn't let the station operate.

BTW, I've duplicated this hang with 2 T238+'s.  I can see why one wouldn't 
want to wipe the sensor cache/memory on each power failure as then you 
won't have reliable remote operation.  Maybe chalk it up to one bad sensor 
interface.

I'll keep trying different combinations and other sensor mixes to see if 
it really is that sensor just working only once the first time, then not
subsequent times.

Thanks,

On Sun, 16 Jun 2013, William Beals wrote:

> Bill:
>
> At least in theory, the T238 shouldn't hang.  There may be some reason why
> though.  Something good to check in case it is something simple is the state
> of the 1-wire bus.  This can be done with a volt meter.  Is it close to +5V?
> What I am wondering it may be is a sensor that is backwards and getting the
> 1-wire bus into an undefined state.  In parallel I'll go look at the code
> and see if there is a way to get rid of old settings.  I don't recall, but
> there may be.
>
> will
>
> -----Original Message-----
> From: wxsig-bounces at tapr.org [mailto:wxsig-bounces at tapr.org] On Behalf Of
> sbm at ottix.net
> Sent: Saturday, June 15, 2013 4:38 PM
> To: wxsig at tapr.org
> Subject: [wxsig] How to make T238+ re-run sensor setup
>
>
> Hi
> 	I have two of these devices (I love them BTW, too bad there aren't
> any more) and they work well.  Recently, I had to replace a whole bunch of
> temp sensors.  Upon plugging into the bus and powering-on the T238+, it
> seems to hang.  I'm suspecting it might be choking on the new sensors being
> new and not finding the old ones.  Is there a way to have the T238+ clear
> its memory of the old serial numbers from the old sensors?  That is, wipe
> clean?
>
> Thanks,
>
> Bill